1/7/2015 8:46 AM | |
Joined: 8/10/2012 Last visit: 4/19/2024 Posts: 14 Rating: (0) |
HI I have V4.1 of Simotion D & TP CAM V4.1.1.15 |
1/7/2015 10:08 AM | |
Joined: 8/10/2012 Last visit: 4/19/2024 Posts: 14 Rating: (0) |
Hi I have V4.1.5.15 |
1/7/2015 11:01 AM | |
Joined: 8/10/2012 Last visit: 4/19/2024 Posts: 14 Rating: (0) |
HI Ok. From where I will get TP V 4.1.5.15? |
1/7/2015 11:42 AM | |
Joined: 8/10/2012 Last visit: 4/19/2024 Posts: 14 Rating: (0) |
hi, I have tried with TP V 4.1.5.15 also, but it gives same error I have order no: 6AU1 435-0AA00-0AA1 |
1/7/2015 11:45 AM | |
Joined: 5/12/2006 Last visit: 4/25/2024 Posts: 22227 Rating: (2980)
|
and which messages are in the diagnostic Log of the simotion? |
11/18/2016 8:19 AM | ||||||
Posts: 6 Rating: (0) |
I have also same error with Simotion D410-2
Can you help me about TP error? |
|||||
11/18/2016 8:50 AM | |
Posts: 6 Rating: (0) |
I am sending all info about my scout version and device version in zip.Could you look please?I connect to the device via ethernet.
AttachmentSIMOTION_D410_2.zip (79 Downloads) |
Last edited by: ismetbjk at: 11/18/2016 8:53:27 AM |
|
11/18/2016 9:16 AM | |
Joined: 5/12/2006 Last visit: 4/25/2024 Posts: 22227 Rating: (2980)
|
diagnostic buffer? from the error in the download windows it looks that something is wrong with the version ot the TP, this can be a defective installation of scout. |
11/18/2016 10:11 AM | |
Posts: 6 Rating: (0) |
Also how can I fix this problem? I am sending diag buffer in attachment.
AttachmentSIMOTION_D410_2.zip (59 Downloads) |
11/18/2016 10:23 AM | |
Joined: 5/12/2006 Last visit: 4/25/2024 Posts: 22227 Rating: (2980)
|
Hi, is there any project data on the D410? Clean all data and then try to download again. Or download the project offline to the CF and then power up the system with the project on the CF Card. Offline Download can be done in the conterxt menu of the PLC (Load to File system) Regards Christoph |
11/23/2016 8:21 AM | |
Posts: 6 Rating: (0) |
Hi I solved Tp Cam problem.Thank you for help. I want to ask a question.How can I connect a external encoder on D410-2 for synchronous operation? I want to connect a line encoder for product length and then servo must be sync on line encoder speed. Can you help me for line encoder connection? |
11/23/2016 8:23 AM | |
Joined: 5/12/2006 Last visit: 4/25/2024 Posts: 22227 Rating: (2980)
|
Hi, encoders can be connected with PROFIBUS/PROFINET direct to the SImotion. Or you use the DriveCLiQ or Encoder interfaces on the SImotion D410-2, then the Encoder is configured in Sinamics a external encoder and you can connect a SIMOTION TO "External Encoder" to it. Regards Christoph |
11/23/2016 9:43 AM | |
Posts: 6 Rating: (0) |
Can I connect X23 port on simotion D410-2? but then The device wants SMC module on hw config?Can you send an example about external encoder configuration on X23 port? |
11/23/2016 9:59 AM | |
Joined: 5/12/2006 Last visit: 4/25/2024 Posts: 22227 Rating: (2980)
|
Hello, yes x23 is possible, is a build in SMC30, so the encoder is work with SMC30 then you can connect it here. To select the X23 interface you must choose "D410_2" in the encoder interface on the Encoder configuration tab. The X23 is assigned to the Sinamics Integrated so you must first configure a encoder in sinamics and then in simotion and connect the Simotion Encoder with the Sinamics Encoder.
Christoph |
Last edited by: ChristophD at: 11/23/2016 10:00:33 AM |
|
11/23/2016 11:39 AM | |
Posts: 6 Rating: (0) |
thank you so much ...I did it. Good works.. |