4/28/2016 5:43 AM | |
Posts: 198 Rating: (36) |
Alarm message PROFINET : no cyclic connection
|
4/28/2016 5:48 AM | |
Posts: 1529 Rating: (202) |
Your CU240 is showing up as an unassigned device. Go to Networks and assign it to the PLC as the I/O controller. |
4/28/2016 5:51 AM | |
Posts: 198 Rating: (36) |
network live view |
4/28/2016 5:55 AM |
|
Posts: 198 Rating: (36) |
already partner port assign what else. from where if any thing other ? |
4/28/2016 6:28 AM |
|
Posts: 198 Rating: (36) |
maintenance required what king of maintenance required because both control unit and power unit are brand new. |
4/28/2016 6:45 AM | |
Posts: 1529 Rating: (202) |
Click on Not Aassigned and select the PLC. Forget the Topology view. |
Last edited by: Jeff Casagrande at: 4/28/2016 6:52:00 AM |
|
4/28/2016 3:44 PM | |
Posts: 198 Rating: (36) |
I assigned with plc s7-1200 but still problem message showing below error {Diagnostic data not available, error in lower-level component} ? |
4/28/2016 3:53 PM | |
Posts: 1529 Rating: (202) |
Did you download the HW configuration? |
4/28/2016 4:00 PM | |
Joined: 5/12/2006 Last visit: 9/20/2024 Posts: 22365 Rating: (3012)
|
go to the diagnostic of the CU240 and show which messages now present. |
4/29/2016 5:20 PM |
|
Posts: 198 Rating: (36) |
|
4/30/2016 10:37 PM |
|
Posts: 198 Rating: (36) |
ERROR SHOWING DIAGNOSTIC DATA NOT AWALABLE
|