I am having almost the same issue with 315F-2PN/DP and F-DI 24xDC24V and F-DO 8x24VDC/2A. On compilation I am getting the same error " The Safety program contains no reintegration for the F-I/O with the start Address (LADDR) 0" I have no HMI on this system and according to the documentation the reintegration should be automatic on the start of the CPU or with the removal of the fault (Have passivation set to individual channel and 1oo1 )" If I need to create a simple reintegration program in the PLC how can this be accomplished???? Splitted from Problem with F-IOs - cant reintegrate IO. |
Last edited by: O_Moderator at: 7/13/2010 8:54 AMLast edited by: O_Moderator at: 7/13/2010 8:54 AMnew subject after splitting |
|
8/3/2010 7:32 AM | |
Joined: 7/28/2010 Last visit: 8/31/2024 Posts: 184 Rating: (11) |
Rockivy, If your issue with Re-Integration hasn't been solved yet,Give me the Siemens order number of theCPU, and I/O card soI can write aPLC code with Re-Integration part based on your hardware. Regards, Behnam www.sigmaprocess.ca |
4/27/2011 3:38 AM | |
Posts: 28 Rating: (1) |
Hello, If FI/O or communicateion is passivate,thenneedacknowledge itwhere Auto or manual mode. so safety program need customer write reintergartionprogramming. you can see the document below: http://support.automation.siemens.com/WW/view/en/22304119 |