10/11/2019 10:48 AM | |
Joined: 5/7/2018 Last visit: 3/24/2023 Posts: 72 Rating: (8) |
Hello, I have a IM155 -6 PN ST (6ES7 155-6AU01-0BN0) device whichhas one faile safe module (6ES7 136-6BA00-0CA0) , one DI and one DO in it. Regards, Gaurav AttachmentIM155.zip (243 Downloads) |
12/14/2020 9:08 AM | |
Joined: 12/3/2020 Last visit: 8/24/2022 Posts: 1 Rating: (0) |
Hi, I have the same problem. Did you solve it ?? Thankyou |
12/17/2020 8:43 AM | |
Joined: 3/11/2019 Last visit: 9/6/2024 Posts: 1569 Rating: (289) |
Hi, please check the type of the used BaseUnit. Which BaseUnit is needed, can be found in the technical data of the used module. For example the module 6ES7 136-6BA00-0CA0 is only compatible bis BaseUnit type "A0". ET 200SP, El-Mod., F-DI 8x24VDC HF"usable BaseUnit A0" Maybe this helps. |
Feedback appreciated, please rate |
|
12/22/2020 11:30 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054)
|
hi together, If you assign F destination addresses to the F IO and you get the message "Modules unavailable", you should check the following points:
When using an ET 200SP you should also check these additional points:
Source: What should you check when the F destination addresses cannot be assigned?
hope this helps, regards, |
Last edited by: mopS04 at: 12/22/2020 11:32:12Last edited by: mopS04 at: 12/22/2020 11:33:07FCK WAR! |
|
This contribution was helpful to2 thankful Users |
Follow us on