please I have this error at cpu314 Event 10 of 10: Event ID 16# 494D |
1/5/2021 4:29 PM | |
Joined: 2/17/2012 Last visit: 9/17/2024 Posts: 21 Rating: (0) |
Hello, We had exactly the same problem - there was a defective module and for some reason it made the PLC go in stop mode. The solution was to disconnect all the modules and then start just the PLC (if it is ok and you have downloaded all the necessary diagnostic OBs it should go in run mode). Then start putting the modules one by one. This procedure should tell you which is the defective module. I am not sure why the PLC cannot diagnose the problem, maybe it has something to do with the backplane bus. Regards |
2/4/2022 9:57 AM | |
Joined: 7/21/2016 Last visit: 7/19/2024 Posts: 20 Rating: (0) |
Hello to all. I want to talk about my experiments)). I have a similar problem ID494D on the PLC 6ES7313 5BE01-0AB0 v2.0.11 I was wondering what was the cause of the problem, I dismantled the PLC. |