10/29/2012 2:11 PM | |
Joined: 5/18/2006 Last visit: 10/21/2020 Posts: 170 Rating: (64) |
What greenberetstated is absolutely true. However, if you are using Safety Matrix you can use the Effect Process Pass Through (PPT) option. You will still need a convert block to go from non-safe 'white' logic to safe 'yellow' logic. But just configure a PPT in the Effect with an external Tag (#PPTx) then wire the valve block output to the PPTx Safety Matrix input (through the convert block). The Safety Matrix ensures (and is TUV Certified to do this) that the safety signal overrides the non-safety PPT signal and provides indication. cabreytj |
This contribution was helpful to1 thankful Users |
11/7/2012 12:56 PM | |
Joined: 8/23/2012 Last visit: 8/20/2024 Posts: 118 Rating: (4) |
I did test f-program (if want download and test this - password for CPU -111, password for F-program - 111). It is correct f-program ... ? AttachmentSafety_a.zip (151 Downloads) |
Last edited by: Eli_47 at: 11/8/2012 7:23 AMChange project language to neutral Last edited by: Eli_47 at: 11/7/2012 1:34 PMSp |
|