9/5/2017 5:11 AM | |
Joined: 9/9/2015 Last visit: 9/15/2024 Posts: 727 Rating: (278) |
Dear everyone We are facing some issues with Sitrans Library, FB2613, SipPS2 block. There are two issues now. The first one is, the block output "QWronDev" keep showing "1". The second is local and remote mode for the Sipart valve showed a quality code of "16#60" in the output of RbkLi. For the first issue, the SIPART faceplate displayed a "Wrong Device" in red color. After we troubleshoot, we saw there is one output I/O, QWronDev writing 1. Then we checked on the gsd as well as instrument. We used PDM V9.0 to indentify the Sipart version. We confirmed that we used the correct gsd with correct instruments. (See picture 4, 5 and 6). How to remove this error? For the second issue, we received Status of 16#3F from the Sipart instruments when it changed from remote to local mode. (see pictures 1, 2,3, 7 ). The output will change to 16#60, simulation quality code. Instead of showing local mode, it show a simulation mode. May i know how to match the sipart instrument with this template? (This template was retrieve from Sitrans Library V6.0. If anyone has any ideas / experience in this, do let me know. Thank you!!!
Attachment20170903_Sipart Issues.zip (106 Downloads) |
Please give me 5 stars Rating if my post is helpful for you. :) |
|
9/5/2017 10:59 AM | |
Posts: 14 Rating: (6) |
Hi JazTai, please have a look at the document "Devices in the SITRANS Library V6.0": The document shows all devices that are integrated in the SITRANS Library. Maybe that's the reason why you get the message "wrong device". Hope this helps. Here you find the application example "Configuring temperature acquisition using SITRANS TH300 in PCS 7 using the SITRANS Library" : Regards Saarlodri |
Last edited by: Saarlodri at: 9/5/2017 11:01:12 AMLast edited by: Saarlodri at: 9/8/2017 11:07:48 AM |
|
This contribution was helpful to1 thankful Users |
9/5/2017 5:36 PM | |
Joined: 9/9/2015 Last visit: 9/15/2024 Posts: 727 Rating: (278) |
I saw a asterisk saying that this is only for s7400 single cpu system. But im using redundant PLC. Yea, i cant find 6DR5520 in the pdf. I will drop Albert an email ask for the reasons now. If i got new information, i will update it here. Thank you so much. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|
9/7/2017 8:37 AM | |
Joined: 9/9/2015 Last visit: 9/15/2024 Posts: 727 Rating: (278) |
Here are Siemens Replied:" The Sitrans Library is only released for single systems. Redundant H-Systems are not supported at the moment from the most profibus pa field devices. The cyclic communication is working well and also the acyclic communication via secondary master e.g.: SIMATIC PDM. We have already solved the issue by using PCS 7 APL library. Thank you everyone. |
Last edited by: JazTai at: 9/7/2017 8:47:30 AMPlease give me 5 stars Rating if my post is helpful for you. :) |
|
Follow us on