8/9/2016 8:56 AM | |
Posts: 567 Rating: (107) |
Hi, I think there are some connections missing. There is only "PZDIn1" connected to an input word. It should also "PZDIn2" connected. Also the output words have no connection. You should read the APL manual chapter 15.6 and the application example "Configuration of Frequency Converters with the APL Channel Block „FbDrive” in SIMATIC PCS 7". You find the manual under the following link: https://support.industry.siemens.com/cs/ww/en/view/109482346 You can find the application example under the following link: |
This contribution was helpful to1 thankful Users |
8/9/2016 4:53 PM | |
Posts: 51 Rating: (0) |
Yes, look that picture: Starting motor: the status flashing (while monitoring time - waiting motor run) and then... Print2: i got control error message. |
8/10/2016 12:32 AM | |
Posts: 51 Rating: (0) |
Hi Berg, Now I connect as you said but still got the same problem. Do you known what else i can change? So jumbled here.. :( |
8/10/2016 1:42 PM | |
Joined: 10/26/2011 Last visit: 9/9/2024 Posts: 762 Rating: (191)
|
Make sure that the start addresses of the input and output addresses begin with the same start value. |
SIMATIC PCS 7 - Overview |
|
8/10/2016 2:39 PM | |
Posts: 51 Rating: (0) |
Hi Thunderstorm, Input and output adresses are the same. |