5/28/2014 5:41 PM | |
Joined: 3/15/2011 Last visit: 9/18/2024 Posts: 134 Rating: (9) |
Dear Sir, I have a Sinamic G120 Drive With CU 240B Control Card.I Configured the drive for local & Remote Configuration. during remote it is taking the SP and Start/stop from Profibus, During Local Stat/ Stop is from terminals and Set point is Fixed set point. But the problem is When it is in local mode if any profibus fault occur's Drive is stopping due to the Fault code : F1916. But my client requirement is during the local mode even profibus fails drive should not stop. so can any one please help on this issue. Regards, Avinashkrishna bh. Hi, You can use P2100 and P2101 to mask the profibus Fault. But you should use it as your last option. regards Ashutosh AttachmentFAULT_MASKING.pdf (166 Downloads) |
This contribution was helpful to1 thankful Users |