7/19/2012 9:12 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
|
Hello, Have a look at attached pdf for calibration procedure. Regards, Marcjan AttachmentInput Calibration.pdf (238 Downloads) |
Problem solved? |
|
7/19/2012 5:56 PM | |
Joined: 2/25/2012 Last visit: 8/26/2024 Posts: 25 Rating: (0) |
Hello To serve the DPI number 1 and 2 in the EM231 module of 8 analog inputs? What are the channels 6 and 7? Regards
|
7/19/2012 8:05 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
|
Hello, That part off the manualis about the 8 channel AI module(0-7) all channels can be set as voltage input, the last 2 (6,7) can allso be set as Current inputs. Regards, Marcjan |
Problem solved? |
|
7/21/2012 2:12 PM | |
Joined: 2/25/2012 Last visit: 8/26/2024 Posts: 25 Rating: (0) |
Thank for the reply On Monday, I reform the electrical box and then I tell you that just came out whole. Regads
|