11/26/2019 3:27 AM | |
Joined: 9/27/2006 Last visit: 9/24/2024 Posts: 12282 Rating: (2685)
|
Hello Iyyappan S.; These part numbers designate I/O modules of the S7-1500 family. To use them over Profibus-DP or Profinet (which is why you would need a gsd file) you must install them as part of a ET 200MP distributed I/O station, which uses S7-1500 modules, with a specialized head module for Profibus or Profinet. The gsd/gsdml files for the IM 155-5 xx ST modules contain the list of modules from the S7-1500 family, for you to select upon configuration. This manual will guide you, and the download sited for the gsd and gsdml files are found below: S7-1500, ET 200MP manual : https://support.industry.siemens.com/cs/us/en/view/59191792 IM 155-5 DP ST gsd file :Profibus-DP https://support.industry.siemens.com/cs/us/en/view/80206700 IM 1455-5 PN ST gsdml file: Profinet https://support.industry.siemens.com/cs/us/en/view/68189683 Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
12/20/2019 9:46 PM | |
Joined: 12/6/2006 Last visit: 7/8/2024 Posts: 92 Rating: (0) |
Thanks dChartier Resolved the issue with your response |
This contribution was helpful to1 thankful Users |