1/4/2021 8:04 PM | |
Joined: 2/24/2020 Last visit: 5/18/2022 Posts: 7 Rating: (0) |
Sorry, my bad. I mean lower! |
1/4/2021 8:14 PM | |
Joined: 12/18/2014 Last visit: 9/22/2024 Posts: 33813 Rating: (4201)
|
I hope I have you understand correct. You didn't write which LOGO! device you exactly have. That's the reason why I made the program for a 0BA8.Standard. AttachmentPressure+speed_control_0BA8.Standard.zip (164 Downloads) |
1/4/2021 8:21 PM | |
Joined: 12/18/2014 Last visit: 9/22/2024 Posts: 33813 Rating: (4201)
|
Hello rickmoerman, you're welcome ... |
This contribution was helpful to1 thankful Users |
1/5/2021 10:27 AM | |
Joined: 2/24/2020 Last visit: 5/18/2022 Posts: 7 Rating: (0) |
Hello Goodmorning everyone, I upgraded it. I have another question. If the pressure sensor is broken, so the value falls below 4 mA, then output Q1 and Q2 should not switch. how do i make this? AttachmentOil Protection.zip (159 Downloads) |
1/5/2021 10:31 AM | |
Joined: 12/18/2014 Last visit: 9/22/2024 Posts: 33813 Rating: (4201)
|
There is only a shortcut to the file in the folder. The file itself is missing. |
1/5/2021 10:34 AM | |
Joined: 2/24/2020 Last visit: 5/18/2022 Posts: 7 Rating: (0) |
Sorry, my mistake here is the file
AttachmentOil Protection.zip (140 Downloads) |
1/5/2021 10:50 AM | |
Joined: 12/18/2014 Last visit: 9/22/2024 Posts: 33813 Rating: (4201)
|
I added two more threshold triggers. These have "0-20mA" as a sensor type. 0 mA corresponds to 0 units, 4 mA corresponds to 200 units. The output of the threshold trigger switches on at 0,0 mA and off at 3.8 mA. You only have to specify where you connect the outputs of the threshold triggers.
AttachmentLub Oil_V2.zip (143 Downloads) |
This contribution was helpful to1 thankful Users |
1/5/2021 11:14 AM | |
Joined: 2/24/2020 Last visit: 5/18/2022 Posts: 7 Rating: (0) |
Amazing!! Thanks a Lot! |
This contribution was helpful to1 thankful Users |
1/5/2021 2:55 PM | |
Joined: 12/18/2014 Last visit: 9/22/2024 Posts: 33813 Rating: (4201)
|
|
Follow us on