Hello suresh; Please verify if you present system meets the hardware/software requirements for CiR (Confguration in Run), which is what Siemens calls the hot-swapping method it applies.They is described in this manual: SIMATIC STEP7 V5.5 Modifying the System during Operation via CiR In particular (extracted from the introduction to that manual): To enable CiR, the user program must meet the following requirements: The program may not include elements that switch the CPU into STOP mode in the event, for example, of a station failure or module error. The following OBs have to be on your CPU: • Hardware interrupt OBs (OB 40 to OB 47) • Timeout OB (OB 80) • Diagnostics interrupt OB (OB 82) • Removal/Insertion OB (OB 83) • Program runtime error OB (OB 85) • Module rack error OB (OB 86) • I/O access error OB (OB 122) Hope this helps, Daniel Chartier |
10/14/2012 7:50 AM | |
Joined: 11/8/2011 Last visit: 8/21/2024 Posts: 387 Rating: (43) |
Hi mms suresh, have you downloaded OB 85,86,87, then you will be able to replace module online . Here you can find the detaills Hope this helps |