Hello. Rated armature voltage of motor is set via P101, also check all start-up procedure (including optimization runs) in the manual, chapter 7.5. |
3/25/2016 7:24 AM | |
Joined: 8/25/2006 Last visit: 4/18/2024 Posts: 2203 Rating: (277)
|
Hello. What are the rated motor data? |
3/25/2016 8:15 AM | |
Posts: 57 Rating: (0) |
KW: 7.5 Arm Volt: 400V Arm Current: 21A Field Voltage: 220V Field Current: 1.56A RPM: 1500 |
3/25/2016 8:30 AM | |
Joined: 8/25/2006 Last visit: 4/18/2024 Posts: 2203 Rating: (277)
|
Did you make speed controller optimization (P051=26) after P051=25? |
3/25/2016 8:54 AM | |
Posts: 57 Rating: (0) |
yes |
3/25/2016 9:52 AM | |
Joined: 8/25/2006 Last visit: 4/18/2024 Posts: 2203 Rating: (277)
|
May be you need to make manual optimization of speed controller to remove fluctuations. 3. Did you check P115? 4. By default in 6RA70 P082=2 (standstill field after line contactor drop). Check the value of P257 or use P082=1 or 3. |
3/25/2016 12:25 PM | |
Joined: 2/9/2013 Last visit: 1/6/2024 Posts: 11 Rating: (0) |
check the actual Field Resistance after removing motor terminals using meter. |
3/27/2016 12:42 PM | |
Posts: 57 Rating: (0) |
P082=1 The field is switched with the line contactor. . |
4/1/2016 9:57 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Is the problem solved? |
4/4/2016 8:46 AM | |
Posts: 57 Rating: (0) |
Yet Not Solved. Still the problem is existing. Field voltage is increasing gradually. |
4/5/2016 5:26 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Could you please attach here parameter list of this drive? |