10/19/2009 3:57 PM | |
Joined: 5/28/2008 Last visit: 9/11/2024 Posts: 1343 Rating: (141) |
Hi, CPU226 don't support profibus, so you need a EM277 Profibus-DP Module. regards |
12/15/2009 6:21 PM | |
Joined: 10/24/2005 Last visit: 8/26/2024 Posts: 14 Rating: (3) |
Hello Sharry, Sory for "the others" but the S7-200 as the capability to communicate with the onboard port on Profibus, but the limitation is the speed, max 187.5 kbps! And sure you need a master on the bus but your HMI can do it. See PDF: Sinamics S120 AC-S7 200_en.pdf Ok the example was made with S120 but at the time of the publication of the document, S110did not exist. Besides that, according to time that you have,during January 2010, it should havea new Firmware with the USS functionality on S110 CU305DP onboard. Have a good day, Denis.. AttachmentSinamics S120 AC-S7 200_en.pdf (485 Downloads) |