Hi All I'm doing some work on a PCS7 installation where they used to map RTD temperatures from another system. In the CFC for the Temperature they used a Pcs7AnIn to read the mapped temperature and then to a MonAnL for the WinCC Problem is they left this when they installed the ET200 I/O and instead of mapping the Real I/O i.e. IW 94 to the Pcs7AnIn they modified the FC and mapped the input and still using the DB to write to the PV_In on the Pcs7AnIn. Obviously they arent using the block correctly and the Module driver is not generated or connected. I'm now changing it so the Real I/O is connected but I'm having issues. Do I still use the Pcs7AnIn and if so how do I set the Range for this RTD Input? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 09/28/2020 11:44:45New subject after splitting |
|
10/8/2020 8:01 AM | |
Posts: 3 Rating: (0) |
Thanks Heisenberg2 Sorry for the late response but under a lot of pressure getting this job out. Did what you explained and all great now. |