9/6/2011 8:45 AM | |
Posts: 86 Rating: (1) |
Any Ideas? |
9/6/2011 11:26 AM | |
Posts: 86 Rating: (1) |
Dear Navnag, First I`d like to thank you alot for your response. please be informed that I have found that the maximum number of WinCC connections (TCP/IP) is 64 for SoftNet and 60 for HardNet -as stated in "WinCC V6 Communication Manual" Page 58 (attached)- but i found also that the number of possible connections for CP1623 is 120 - stated in its manual- so i want to know how many PLCs could be connected actually to WinCC -through TCP/IP- and what will be the right produre to follow if i exceed that limit. AttachmentWinCC Communication Manual P.58.pdf (2913 Downloads) |
Last edited by: EULER1313 at: 9/6/2011 11:28 AM |
|
11/27/2019 9:52 AM | |
Joined: 10/8/2018 Last visit: 4/18/2024 Posts: 3 Rating: (1) |
Hello Everyone, In case of SIMATIC S7-protocol Suite Driver you can configure8 PLCs(S7-300/S7-400),without using any CP card. In SIMATICS7-1200/S7-1500 driver you can configure upto64 S7-1200 PLCs and 128 S7-1500 PLCs. Thank you. Attachmentmk_@MSITStore_C__PROGRA~2_Siemens_WinCC_documents_English_Perfo.pdf (764 Downloads) |
Last edited by: RUSHIKESH POTALE at: 11/27/2019 10:06:59 |
|
2/15/2020 10:54 AM | |
Joined: 10/2/2015 Last visit: 7/22/2024 Posts: 5 Rating: (0) |
Hi, this is how I solved the problem: https://github.com/Jaroslav-Dvorak/S7conn_extender |