8/2/2016 3:45 PM | |
Posts: 38 Rating: (0) |
Yes it is set to do frequency. How to download the hardware configuration please. |
8/2/2016 3:54 PM | |
Posts: 38 Rating: (0) |
oh thank you, yes now it starts to read but not real value with max of 26 |
8/2/2016 5:19 PM | |
Posts: 38 Rating: (0) |
Hi, Attached is the HSC configuration as per MR. William design, and for the working environment I think this very good suggestion as I've tried different designs and they didn't work smoothly. I'm waiting for your commentary and thank you for the advice. Regards.. Okod. AttachmentQuadrature Encoder.pdf (311 Downloads) |
8/2/2016 7:56 PM | |
Posts: 38 Rating: (0) |
Thank you. |
8/2/2016 9:58 PM | |
Joined: 7/7/2010 Last visit: 9/23/2024 Posts: 15217 Rating: (2417)
|
Does it properly track the RPM as you expect? If so, that's great.
|
science guy |
|
8/3/2016 1:01 PM | |
Posts: 38 Rating: (0) |
Yes it is ok, 8 counts make one revolution however there is a slight difference but it's acceptable. Thank you. |
This contribution was helpful to1 thankful Users |
8/3/2016 6:48 PM | |
Posts: 5225 Rating: (1192)
|
You may consider the use of the CTRL_HSC_EXT. AttachmentEXTRACT_Instruction CTRL_HSC_EXT.pdf (341 Downloads) |
8/3/2016 7:11 PM | |
Posts: 38 Rating: (0) |
Ok, I will see, check and update as possible. Thank you very much Mr. William. |