1/12/2018 5:34 PM | |
Joined: 11/2/2016 Last visit: 7/10/2019 Posts: 62 Rating: (0) |
I've already done it,but an error appears, see attached file. |
1/12/2018 5:39 PM | |
Posts: 8946 Rating: (999) |
You must use WinCC advanced TIA ES V14 (engineering System v14) to Import the HMI - File, NOT the runtime-File (.fxc)! |
1/12/2018 6:07 PM | |
Joined: 6/3/2014 Last visit: 1/17/2023 Posts: 660 Rating: (193) |
Hello, after updating the project version from V13 SP1 to V14 you need to change the image version of your Runtime Advanced in the project, too. The version of the runtime installation and the image version of the runtime that is configured in the project need to be the same. The following FAQ shows you how to do that: --> first: "Automatic upgrading of the project", then "Updating the Image version" Greetings, H.J. |
Last edited by: H.J. at: 1/12/2018 6:11:59 PM~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ★ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ |
|
1/12/2018 6:10 PM | |
Posts: 8946 Rating: (999) |
here a screenshot: Check if Setting is OK (V14 or V14.1 if SP1) |
Last edited by: IBN-Service at: 1/12/2018 6:11:40 PM |
|