3/14/2014 6:02 AM | |
Posts: 146 Rating: (0) |
Anyone please help me ! Thank you very much ! |
3/14/2014 10:53 AM | |||||||||||||
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
|
Hello, You can download the scaling blocks here :How can you scale analog values with S7-200 in conjunction with CPU224XP and expansion modules EM 231, EM 232 and EM 235? There is a description of the blocks too. Use the S_ITR function.
Ov is a real value you can send to the panel Iv is your analog input i.e. AIW0 Osh is the max output of the scaled analog value i.e. 50.0 Hz Osl is the min output of the scaled analog value i.e 0.0 Hz Ish is max analog input value i.e.32000 (check that with Chart status) Ish is min analog input value i.e 0 If any more questions please return with some details of the problem (printscreen) Edit: this is the PLC part of the answer, if you have trouble with micromaster part, post new question there. Regards, Marcjan |
||||||||||||
Last edited by: Marcjan at: 3/14/2014 4:11 PMLast edited by: Marcjan at: 3/14/2014 10:54 AMProblem solved? |
|||||||||||||
This contribution was helpful to2 thankful Users |