6/26/2013 8:45 AM | |
Posts: 153 Rating: (2) |
Can we multiple HMIs with S7-200 on PPI??? What can be the maximum distance between HMI and PLC ?? |
6/26/2013 8:49 AM | |
Joined: 4/24/2006 Last visit: 9/23/2024 Posts: 8742 Rating: (1168) |
Hello P,abs, Perhaps this link might help: Which HMI components can you connect with S7-200 CPU and what should you watch out for when doing so? Best regards, Wizard |
This contribution was helpful to1 thankful Users |
6/26/2013 8:52 AM | |
Posts: 153 Rating: (2) |
could you give me some link regarding distance on PPI?? |
6/26/2013 9:05 AM | |
Joined: 4/24/2006 Last visit: 9/23/2024 Posts: 8742 Rating: (1168) |
Hello, I did not found a link about PPI, but I found one about MPI: What should you watch out for when using the RS485 repeater in PROFIBUS and MPI bus systems? Here is a link to manual: S7-200 System Manual Perhaps you find the information in chapter 7 Best regards, Wizard |
7/8/2013 12:16 PM | |
Joined: 11/21/2007 Last visit: 8/12/2024 Posts: 2325 Rating: (308) |
Hello William Bis right .. you can connect more than one HMI to S7-200. for example the TD-200 manual shows how you can connect 2 Nos. TD-200 to same S7-200 CPU by defining two seperate parameter blocks in the CPU. Here is an extract from the S7-200 Manual giving the No of connections possible for S7-200 PPI Protocol PPI is a master-slave protocol: the master devices send requests to the slave devices, and the slave devices respond. See Figure 7-7. Slave devices do not initiate messages, but wait until a master sends them a request or polls them for a response. Masters communicate to slaves by means of a shared connection which is managed by the PPI protocol. PPI does not limit the number of masters that can communicate with any one slave; however, you cannot install more than 32 masters on the
Port 1 9.6 kbaud, 19.2 kbaud, or 187.5 kbaud
AttachmentS7-200_PPI_Protocol.pdf (233 Downloads) |
Last edited by: Navnag at: 7/8/2013 12:17 PMThere is no such thing as the last bug in a program |
|