Industry Online Support
Technical Forum
10/5/2008 10:37 AM | |
Joined: 9/27/2006 Last visit: 9/19/2024 Posts: 12282 Rating: (2684) |
Hello callsg; The standard Siemens is refering to on their datasheet for the Relay Output module of the S7-400 family is IEC 647-5-1. This describes the make-before-break characteristics of small powercontrol circuits. You can have an idea of how to apply the standard on the following document: http://www2.sea.siemens.com/NR/rdonlyres/7DBFE5E3-A53F-40DF-9603-69F5867B516E/0/Control_Circuit_Classifications.pdf For the complete standard documentation, you will have to purchase it at a IEC webstore, such as this one: Or you can borrow it from someone who has it in their library... http://www.iec.ch/webstore/custserv/faqs/faqs_buying.htm Now, I hope you realize that this standard will not help you determine the number of operations that a relay output can be expected to produce. Siemens garantees 100,000 operations of their relay outputs at certain voltage and current rating described by the IEC 647-5-1 standard. If your power ratings in the field are lower than the limits then you will probably extend the operating life of the electro-mechanical relays on the board. But there are noequations available in the standard to calculate this. Hope this helps, Daniel Chartier |
10/14/2008 8:06 AM | |
Posts: 17 Rating: (0) |
Thank you for your answer. I have already understood that standard. The current of site is low than the standard. I can get longer life of relay. |