3/22/2020 12:45 PM | |
Joined: 9/27/2006 Last visit: 9/24/2024 Posts: 12282 Rating: (2685)
|
Hello Tomy; You can enable. disable and delay specific diagnostic OBs in the user program of a S7-300 or S7-400 CPU in Simatic Manager, using specialized SFCs. This is explained in Chapter 12 of the System and Standard Functions manual: https://support.industry.siemens.com/cs/ww/en/view/109751826 Outside of these "external" functions, internal evaluation of the diagnostic messages.by the user program must use the local variables of the diagnostic OB to read out the fault. In TIA Portal there are specialized functions, such as can be seen here: https://support.industry.siemens.com/cs/ww/en/view/78380025 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 03/22/2020 12:55:44Last edited by: dchartier at: 03/22/2020 13:07:45 |
|
This contribution was helpful to1 thankful Users |
3/22/2020 2:22 PM | |
Joined: 5/4/2009 Last visit: 5/28/2024 Posts: 914 Rating: (40) |
Thank you again sir, I will check it up, and reply to you soon. Regards. Tomy |
Aim Higher |
|
3/22/2020 3:34 PM | |
Joined: 9/21/2012 Last visit: 9/24/2024 Posts: 4165 Rating: (464) |
Now is a good point to actually start reading the manual, and understand how to use diagnostics in OB's. |