4/21/2018 1:41 PM | |
Joined: 9/27/2006 Last visit: 9/20/2024 Posts: 12282 Rating: (2684) |
Hello Isagram; The module you show is an Interbus coupler form Phoenix Contact: https://www.phoenixcontact.com/online/portal/ca?uri=pxc-oc-itemdetail:pid=2726188&library=caen&tab=1 It is similar to an ET 200_ station, that works on Profibus or Profinet, except that it is designed for Interbus, a different network of remote I/O supported by Phoenix Contact. If you are interested,you will find in this link the basic information on Interbus: http://www.interbus.de/dl/Dok_interbus_basics_en.pdf The system will work only if there is a Interbus master processor in the S7-400 rack, such as this one: https://www.phoenixcontact.com/online/portal/ca?uri=pxc-oc-itemdetail:pid=2719962&library=caen&tab=1 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 4/22/2018 8:06:46 PM |
|
This contribution was helpful to1 thankful Users |
4/21/2018 2:02 PM | |
Posts: 241 Rating: (1) |
thank you ,yes the module you mentioned is in the cpu 400 rack ,can i simulate a simple configuration of interbus in the hw config ? |