4/24/2011 8:52 PM | |
Posts: 86 Rating: (7) |
Hi, Seems like a bad connection. I think when you disconnect the ethernet cable you have the same behavior. Yer |
6/4/2011 9:55 PM | |
Posts: 55 Rating: (4) |
It happens even if there is one chart open while watch 6 or less points. There are no cable problems. |
6/5/2011 7:55 AM | |
Posts: 691 Rating: (37) |
Dear Phantom75 Myself also facing same problem as Kris C. For your Information I am running WinCC Runtime on Ethernet and Opening 3-4 charts and going online |
6/5/2011 9:20 AM | |
Joined: 5/24/2007 Last visit: 4/24/2024 Posts: 284 Rating: (27) |
Hi Check the following 1. Scantime in PLC? is it what you set or is it much more 2. Communications jobs ? Is it close the maximum number 3. Check the network? Lot of free tools are there to check this. Mainly watch for Packet Collissions 4. Check the actual data exchange on the network? Use Wire Shark. 5. Check the computer connections. Use the tools from www.sysinternals.com to find out how many open connections are there and check if you have something which you are not expecting.particularly on the network which you are using for your PG/PC Interface. Krish |