Joined: 9/27/2006 Last visit: 9/19/2024 Posts: 12282 Rating: (2684) |
Hello samad; Here is waht the Equipment manual for the xP270 HMI panels says about your error message: http://support.automation.siemens.com/WW/view/en/10420917 190011Possible causes: 1. The value entered could not be written to the configured PLC tag because it was either above or below the value range: The input is rejected and the original value is reset. Remedy: Ensure that the value entered is within the value range of the PLC tags. 2. Connection to the PLC has been interrupted. Remedy: Check the connection to the PLC. |
Last edited by: dchartier at: 10/19/2008 9:37 AM |
|