2/25/2020 5:52 AM | |
Joined: 4/28/2017 Last visit: 3/14/2024 Posts: 149 Rating: (24) |
Hai reypapin, It says that, unable to write the Graphics templates. There might be a mismatch between your OSSVR PC station running project and the backup available on ES Pc. (the .pdl picture not synchronized properly. Somebody might have worked directly on server PC and haven't copied that changes to ES project folder) Please try by deactivating the server 02 (server 01 should be active) and close WinCC manager by "Close project and exit" after that try to do the project download again from ES Pc. If not succeeded, restart the server 02 stations. I have considered Server 01 as a downloaded station already as you mentioned. |
Last edited by: Maruthakasi_S at: 02/25/2020 05:56:53Last edited by: Maruthakasi_S at: 03/01/2020 10:39:41Note: If this post did really help you, you may use the "Rate" button to express your support, Thank you. |
|
This contribution was helpful to1 thankful Users |
3/1/2020 10:45 AM | |
Joined: 4/28/2017 Last visit: 3/14/2024 Posts: 149 Rating: (24) |
Hai reypapin, sorry for the delayed response, You can try the following thing. In this case, it better to go on another way, Please do an entire compilation of OS with the following scope (As Tags and messages, Memory reset, SFC Runtime, (Don't choose picture tree) Then, Change your active project destination path configured under your OS station property. Try to download the project to a new location. If it's successful, you can do the download to another Server as well once after ensuring the successful synchronization of Uarchive groups. |
Note: If this post did really help you, you may use the "Rate" button to express your support, Thank you. |
|