Joined: 9/27/2006 Last visit: 9/21/2024 Posts: 12282 Rating: (2684) |
Hello renay; If you open the following manual: SENTRON PAC4200 Power Monitoring Device System Manual |
7/23/2013 5:25 AM | |
Posts: 262 Rating: (45) |
Hi, Should i tell you the easiest and best way of configuring PAC 3200/ 4200 devices? Leave the RS485 module which are mounted as it is... Find out an unmanaged ethernet switch and connect all PAC 3200/ 4200 & Server PC with this switch through a Cat5 cable. Load the powerconfig software, from the below link ( hope you would have receievd a CD containing this softwarein PAC 4200 box) https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&objId=57887187&nodeid0=22951684&load=content&lang=en&siteid=csius&aktprim=0&objaction=csview&extranet=standard&viewreg=WW After downloading, you will be able to see all the PAC 3200 and PAC4200 in the powerconfig ( use option search for accessible device) Do the IP addressing of these devices and press online measure vaule in the same software. Once, this is done, you can see configure these meters in PowerManager Software also. Still you want to use RS485 communication architecture then pls inform... it will only haper your speed of data updation at PC. AttachmentArchitecture_Ethernet.pdf (429 Downloads) |