10/2/2020 9:20 AM | |
Joined: 4/18/2014 Last visit: 9/25/2024 Posts: 253 Rating: (5) |
Wow thats great advise..... Thanks |
10/2/2020 12:13 PM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804)
|
Hello, the speed setpoint is transferred as a percentage value referred to p2000 and following parameters. So the easiest way would be to do the conversion on PLC side an provide the adequate setpoint in percent to the SINAMICS. Please see chapter 6.6.2 of the fieldbus manual for more details. https://support.industry.siemens.com/cs/ww/en/view/109757336 |
With best regards, |
|
This contribution was helpful to1 thankful Users |
10/4/2020 7:36 PM | |
Joined: 5/22/2012 Last visit: 3/24/2022 Posts: 895 Rating: (67) |
What is p2000 What is in r2050[1] if you use Telegramm 1 ? |
10/5/2020 3:16 AM | |
Joined: 4/18/2014 Last visit: 9/25/2024 Posts: 253 Rating: (5) |
Please find the attached document for your reference. And also i never found the r2050[1] in VFD Parameter. Thanks in advance. AttachmentVFD.docx (323 Downloads) |