9/24/2010 4:14 PM | |
Posts: 25 Rating: (9) |
Waterlily, There is a block in the CFC Library called AFP which I think will help you. It allows you to enter parameters for the off time and on time for the clock output. It is also described in the CFC library manual in chapter 1.14.5 which you can download from the following link: http://support.automation.siemens.com/WW/view/en/24451026 Hope this helps. Regards, Nick |
This contribution was helpful to2 thankful Users |
9/25/2010 10:53 AM | |
Posts: 27 Rating: (0) |
Hi Nick, I was looking for a specific block. I will test this block and come back with result:-) Regards, |
9/28/2010 4:03 AM | |
Posts: 27 Rating: (0) |
Hi Nick, I used this block. It is fine:-) Thanks, |
This contribution was helpful to1 thankful Users |
10/20/2015 11:15 AM | |
Posts: 10 Rating: (0) |
Here is the representation of the blocks in TIA V13. |
10/21/2015 9:17 AM | |
Posts: 10 Rating: (0) |
You are totally right , the timing in ON/OFF state is not the same. Can you please upload a graphical descripton of your solution? |
10/22/2015 9:09 AM | |
Posts: 10 Rating: (0) |
I think this type of hardcoding can't be done in TiA portal..anyway still need to check it..!!! I need ON/OFF starting from 5ms or lower until 50ms....!!! |
10/22/2015 3:01 PM | |
Joined: 1/15/2009 Last visit: 4/19/2024 Posts: 316 Rating: (40)
|
Hi Mathias, While I may know a thing or two in PCS 7, I am by no means even average with TIA Portal. I would recommend posting the question to our TIA Portal Forum instead of PCS 7 group, https://support.industry.siemens.com/tf/ww/en/threads/243/?page=0&pageSize=10 |