6/29/2013 11:52 AM | |
Joined: 4/17/2012 Last visit: 8/30/2024 Posts: 474 Rating: (10) |
Hi, please find the attchment.some important points to check???
|
7/7/2013 4:18 PM | |
Joined: 2/1/2011 Last visit: 9/13/2023 Posts: 186 Rating: (4) |
Dear Sir, Thanks For replying to problem and finally problem is resolved. There was no requirement to change in settings from PLC side. At drive side settings have to be made proper. Control Word is to be defined with increasing parameter number and all control word declared is to be defined with parameters. |
This contribution was helpful to3 thankful Users |
7/10/2013 4:21 AM | |
Posts: 30 Rating: (7) |
Hi, Your screen showing the communication is up and the initial values have been read out from BAUMULLER drive. but you saing the values are not updated. my investigation is this, from your Area Assignment of I/O, the 1st module you entered is "Non-cyclic data module" , in this case, the processing of the non-cyclic data requests is executed in the PLC with low priority and vales will only be updated upon request. That's the general rule I guess you already knew. and you are not using Non-cyclic area as communication at this case. the area you are concerning are Cyclic Area, which are PID260 and PID264, thats would be the actual value read out from drive., and if you could also attach more screen shots on Input/Output 256~259, also the status/ control word, from that may tellus more about your status.alsotry togglethe control word see how the value looks like. However, I don't think the problem on DP/communction part. Cheers, |
7/10/2013 6:48 AM | |
Joined: 4/17/2012 Last visit: 8/30/2024 Posts: 474 Rating: (10) |
Dear Ashishm, Good work... Thanks for the update
|
Follow us on