Wondered if anybody else had suffered this? Hello paulchadd, Can you post the Diagnostic Buffer entry here?? That helps to understand the fault which occured in the CPU. Moreover you also do create a Support Request, so that Hotline is notified parallely.
|
Like it? Rate it! |
|
10/28/2013 3:58 PM | |
Posts: 3 Rating: (0) |
Hello have attached the diagnostic output. seems to be items 6 and 7. Siemens lists the 1215C as voltage analog output and inputs but they are actually current. so i have put 500 ohn resistor accross out put to take the resultant voltage off. i am using tia v11 basic sp 2 update 5 the firmware of the CPU is 3.0.2
AttachmentDiagnostics.txt.zip (105 Downloads) |
10/28/2013 7:21 PM | |
Joined: 8/31/2010 Last visit: 9/24/2024 Posts: 1521 Rating: (227) |
Hello paulchadd, The Analog output is already of the type 0 - 20 mA refer this Analog Output Specification. Maybe remove the resistor and observe the behaviour. Whereas the AI is of type 0 - 10V (Analog Input Specifications) |