9/22/2014 5:58 AM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hello SagarDPatel, In S7 200 the maximum value is 32000 Have a look: below you can find the library for scaling and a sample project: How can you scale analog values with S7-200 in conjunction with CPU224XP and expansion modules EM 231, EM 232 and EM 235? below how to save the library: How do you incorporate a user-defined library into a project with STEP 7 Micro/WIN and what should you watch out for? How do you use STEP 7 Micro/WIN to create normal program blocks from library blocks? and this thread: Scalling for different data fomats with S7-200 - Siemens Industry ... |
Last edited by: Ste39 at: 9/22/2014 6:35 AMAdd link Last edited by: Ste39 at: 9/22/2014 6:33 AMLast edited by: Ste39 at: 9/22/2014 6:26 AMLast edited by: Ste39 at: 9/22/2014 6:01 AM |
|
This contribution was helpful to1 thankful Users |
9/22/2014 3:06 PM | |
Joined: 11/21/2007 Last visit: 8/12/2024 Posts: 2325 Rating: (308)
|
Hello SagarDPatel Besides what has been suggested by Ste39( Scaling in the PLC ) , you can also easily do the Scaling in the HMI Tag properties also. Just select the "Linear Scaling" option of the HMI Tag and you can set the scaling as per your requirement. ( Pl see attachment ) In S7-200 the Raw valie of Analog input for 0-100% of AI range is 0-32000 while in S7-300 / 400 it is 0-27648. You can scale accordingly. Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
This contribution was helpful to1 thankful Users |
10/8/2014 11:06 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
|
Hello, Please read the S7-200 System Manual From page 426 and further you can learn how to setup, connect the module. How the analog values are represented depends on the setup. Regards, Marcjan |
Problem solved? |
|