I have aproblem in MM440 37 KW some times loss address in profibus network especially when completely powered off . i wish asolution for that |
1/23/2015 5:54 PM | |
Posts: 6 Rating: (0) |
I use S7 400 Make programming by lap top using drive monitor
|
1/24/2015 8:40 AM | |
Posts: 784 Rating: (52) |
Use DIP switches of profibus module to assign address.
|
1/24/2015 9:04 AM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hello alaa rezk Try what our friend Wago says: Getting Started Guide PROFIBUS Module |
This contribution was helpful to1 thankful Users |
1/26/2015 9:21 AM | |
Posts: 6 Rating: (0) |
unforetunately profibus module in drive not include profibus DIP switches Any other solution you think ? |
1/26/2015 2:41 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hello alaa rezk, Are you sure? What code you have onyour Profibus Optional Board? Take a look on Chapter 5: Operating Instructions: MICROMASTER PROFIBUS Optional Board If it is this your Profibus Optional Board try with P=0918 via the BOP/AOP also |