I didn't understand what do you want to do. By default, main speed setpoint comes from terminals 4,5 (sheet G113 in function diagrams, then it flows through sheets G127...G130 and comes to sheet G135 into P644). You multiply P644 by P322, i.e. analog input at term. 4,5 by AI at term. 6,7. The result is your speed setpoint. Regarding F050, are you sure that the power of your motor (it is small, 2.85kW) is sufficient for moving the load? Check that the motor or load is not locked. Look also at theFAQfor manual optimization of speed controller.
|