Industry Online Support
Technical Forum
9/19/2007 1:26 PM | |
Posts: 1275 Rating: (123)
|
Hi, Those errors mean: 410E - Connection has been aborted - PLC or CP has been turned off or reset - PLC not connected to bus or bus system error - Maximum number of permissible connections in ths PLC exceeded 7001 - Connection aborted because of stop check - The connection has been aborted by the channel, because a VMD status of the CPU (STOP, HALT, or DEFECT) has been recognized. Which protocol are you using for communication, and with which communication processor? You said you have a client - server architecture. How many servers and clients? Are the servers used for operation? Best regards, Danielle |
9/19/2007 2:59 PM | |
Posts: 5 Rating: (0) |
Welcome. For communication I using TCP/IP, and processor CP1613 and CP343-1. I have in my architecture 2 servers and 5 clients. Yes there are servers used form operation. Thanks.! Ramzes |
Last edited by: ramzes at: 19.09.2007 15:07Last edited by: ramzes at: 19.09.2007 15:05Last edited by: ramzes at: 19.09.2007 15:02 |
|
9/21/2007 2:25 PM | |
Posts: 1776 Rating: (95)
|
Hi have You checked all other log files. Have You checked Status Driver Connection? See also the Link http://support.automation.siemens.com/WW/view/en/22892720 April |
9/21/2007 4:13 PM | |
Posts: 5 Rating: (0) |
hi yes I checked all other log files, and in WinCC_Sys_02.log there is information about WINCC disconnected and connected to PLC this same time as error code Errorcode 0xFFDF 410E! in log files SIMATIC_S7_PROTOCOL_SUITE_01.LOG. I don't know meybe it's problem in WINCC (skrypt) or another things in WINCC . Ramzes |
9/21/2007 7:07 PM | |
Posts: 3149 Rating: (171)
|
hi how many communication ressources did you set on your S7-CPU? http://support.automation.siemens.com/WW/view/en/299124 nemo |
9/22/2007 10:11 AM | |
Posts: 5 Rating: (0) |
Hi I have: PG communication - 1; OP communication - 2; S7 standard communiaction - 1; Ramzes |
Last edited by: ramzes at: 22.09.2007 10:12 |
|