Dear Diwa, First of all thank you very much for your great postings. Really wonderful. I came across a similar problem with F002. (DC Inverter SIMOVERT VC6SE7041-2WL60-Z). Later we found that one of the CT was faulty. To confirm,we put back the old CT and the same sysmptoms repeated.DC voltage at DC bus and cardterminal was OK.But while 'starting' the drive, a light hissing sound was heard and F002 was displayed. Any experience like it? Best Regards, eskey. Splitted from Common Faults in Masterdrives and their solutions.. |
Last edited by: O_Moderator at: 4/13/2010 12:16 PMLast edited by: O_Moderator at: 4/13/2010 12:16 PMnew subject after splitting |
|
This contribution was helpful to1 thankful Users |
4/12/2010 2:56 PM |
|
Posts: 33 Rating: (2) |
And by the way .. I'll be here for help till you rate my answer |
4/24/2010 6:48 AM | |
Posts: 4 Rating: (3) |
Hi Devesh, Let me put it in this way. What will bethe 'fault display' if any CT is faulty? Thanks, eskey |
7/3/2015 12:32 AM | |
Posts: 5 Rating: (0) |
dear all. Thanks for your discussion. I would lik to add another reason that some times DC link fuses burnt due to IGBT damaged or cable or motor burnt So be carfule don't restart without check these fuses. Thanks
|
8/5/2015 8:54 AM | |
Joined: 8/23/2011 Last visit: 12/5/2019 Posts: 19 Rating: (0) |
Some times also CUVC card is responsible for F002 as the voltage sensing resistor might be faulty on CUVC. |