Hello sir i have a problem with s7-315-2dp cpu with 2 SM-335 analog modules , the eSF led on the two sm-335 modules is lit in red and the cpu SF led is red too making the CPU goes to stop mode when i access the cpu from simatic manager and view the diagnostic buffer the errors are Rack: --- Slot: --- Event 1 of 100: Event ID 16# 494D STOP due to IO error No relevance for user (Z2): 0050 (Z3): 4555 Previous operating mode: STOP (internal) Requested operating mode: STOP (internal) External error, Incoming event 01:24:54.378 AM 08/28/2005 (Coding: 16# 494D FF44 C000 0000 0050 4555) Event 2 of 100: Event ID 16# 4300 Power on backed up Previous operating mode: No voltage Requested operating mode: STOP (own initialization) Incoming event 01:24:50.516 AM 08/28/2005 (Coding: 16# 4300 FFF3 0000 0000 0000 0000) and when i tried to upload station to pc the blocks folder has no DBS,OBS,FBS and FCS only system data does this mean the the program is lost ? and how can i know the cause of the SF error in the two SM-335 modules ? AttachmentDiagnose.txt (45 Downloads) |
8/3/2017 7:48 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1050) |
hi, IO-Error with Error-ID 494D has been discussed many times here in forum. Search for 'Event ID 16# 494D' For me it always seems to be a problem with the backplane-bus. But the best would be, contact Siemens by starting a Support Request. They could give you more information on this error with the coding from the diagnostic buffer: No relevance for user (Z2): 0050 (Z3): 4555 (Coding: 16# 494D FF44 C000 0000 0050 4555) hope this helps, regards, |