4/27/2012 9:16 AM | |
Joined: 2/27/2012 Last visit: 9/15/2024 Posts: 17 Rating: (0) |
AttachmentCU240E-2.pdf (308 Downloads) |
4/29/2012 4:40 PM | |
Joined: 8/25/2011 Last visit: 7/3/2024 Posts: 29 Rating: (4) |
The terminals metinoned in the initial thread were 21 & 22. This is digital output 1. This is a transistor output. AttachmentPages from Control_Units_CU240B-2_and_CU240E-2_en-US.pdf (293 Downloads) |
Last edited by: timmyLDeng at: 4/29/2012 4:47 PM |
|
4/30/2012 9:12 AM | |
Joined: 3/15/2011 Last visit: 9/18/2024 Posts: 134 Rating: (9) |
I HAVE CONFIGURED IT FOR DRIVE RUN ........ I 'M USING EXTERNAL 24 V SUPPLY..... |
4/30/2012 9:17 AM | |
Joined: 3/15/2011 Last visit: 9/18/2024 Posts: 134 Rating: (9) |
THANKS FOR YOUR PROMPT REPLY................... |
4/30/2012 12:53 PM | |
Joined: 11/18/2010 Last visit: 8/5/2022 Posts: 523 Rating: (32) |
hi,ashutosh please don't use external supply use internal supply which DO it self providing, regards, viral patel |
5/1/2012 7:28 AM | |
Joined: 5/28/2008 Last visit: 9/21/2024 Posts: 4515 Rating: (839) |
Here's attached the complete page that you take the capture from it. It is stated clearly the connection when using internal power supply and external power supply as well. The limit for each outpout is 0.5 A. If you have a load powered from DO of the drive and will consume more than 0.1 A, then you should use external power supply, other wise you can use both internal or external power supplies. AttachmentPages from Control_Units_CU240B-2_and_CU240E-2_en-US.pdf (210 Downloads) |
Ayman Elotaify |
|
5/1/2012 12:57 PM | |
Joined: 2/27/2012 Last visit: 9/15/2024 Posts: 17 Rating: (0) |
hii Ayman elotaify, see attechment for difference of second digital output(DO1) between CU240E/S & CU240E-2. hope this is information will help you. AttachmentCu240E-2.pdf (187 Downloads) |
Last edited by: Amit3545 at: 5/1/2012 1:06 PM |
|
5/8/2012 10:41 AM | |
Posts: 205 Rating: (11) |
hi ayman elotaify, i hope you are now clear with this DO type of CU240E-2 series all "-2"series cu |