6/17/2013 10:55 PM | |
Joined: 9/27/2006 Last visit: 9/19/2024 Posts: 12282 Rating: (2684)
|
Hello dre; See this link for an overview of Danfoss VLT Profibus-DP communication: profibus VLT Note that as part of the drive configuration, in Parameter 904 of the drive you have to select a PPOx number. The PPOx structure is a way to determine how many words are exchanged between the PLC master and the drive (it is part of the Profidrive profile in Profibus-DP). It also determines the content of each word exchanged. The manual explains the PPOx options on page 21. On page 29 you will see a description of the Control word usage to start and stop the motor using Profibus-DP: Control word/Status word. The following bit pattern sets all necessary start commands: 0000 0100 0111 1111 = 047F Hex.* 0000 0100 0111 1110 = 047E Hex.* 0000 0100 0111 1111 = 047F Hex. Note: write the 3 hexa values one after the other to the drive CTW address in order to start the motor; the motor controller must see a rising edge at the LSB of CTW in order to start (passage from F to E and back to F provides the equivalent of a rising edge signal). Quickstop: 0000 0100 0110 1111 = 046F Hex. Stop: 0000 0100 0011 1111 = 043F Hex. See also the links posted by our friend Wizard in this thread (there you will find a sample block for Danfoss drives controlled by a Siemens PLC): /tf/WW/en/Posts/75493 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 6/17/2013 11:10 PMLast edited by: dchartier at: 6/17/2013 10:56 PM |
|
This contribution was helpful to3 thankful Users |
6/18/2013 8:52 PM | |
Posts: 2 Rating: (0) |
Thank you for your help. Dre
|