5/25/2014 9:57 PM | |
Posts: 8946 Rating: (999) |
Please try first following in PLC: A DB1.DBX 4.0 S Q 0.0 A DB1.DBX 4.1 RQ 0.0 |
This contribution was helpful to2 thankful Users |
5/26/2014 8:11 AM | |
Posts: 8946 Rating: (999) |
Hello Ayman, very nice link! Thank you for sharing. But I understand the Problem of xuanphuin a different way.... Would you please read the basic question again to tell me if i am wrong...? |
Last edited by: IBN-Service at: 5/26/2014 8:12 AM |
|
This contribution was helpful to2 thankful Users |
5/26/2014 9:19 AM | |
Joined: 5/28/2008 Last visit: 9/9/2024 Posts: 4515 Rating: (839) |
Hello Ayman, very nice link! Thank you for sharing. But I understand the Problem of xuanphuin a different way.... Would you please read the basic question again to tell me if i am wrong...? Thank you,Jürgenfor your notice. My reply here is you already solved the problem and your code provided should work if the symbolic IO field is done correcty. If problem still happen, may be other network in PLC program write inDB1.DBX 4.0 or DB1 DBX 4.1 or even in Q0.0. So, you have to use cross reference to check. Monitoring using VAT will help. Open a VAT while you are changing the selection of symbolic IO field and see what is happening withDB1.DBX 4.0, DB1 DBX 4.1 and Q0.0. Hope this helps.
|
Ayman Elotaify |
|
This contribution was helpful to1 thankful Users |