5/8/2008 5:46 AM | |
Joined: 9/27/2006 Last visit: 9/22/2024 Posts: 12282 Rating: (2685) |
Hello Darius; Here is Siemens has to say about the CYCLE parameter: If the controller blocks are called conditionally (without call distributor), it often suffices to take the time base of the cyclic interrupt. Since the CYCLE parameter is used to calculate other parameters in your block, calculations must be synchronized with the call cycle of the block. If you really need a faster loop, I suggest you change the call time of OB35 and then again make CYCLE equal to that. The FAQ the above extract is taken from can be found here: http://support.automation.siemens.com/WW/view/en/27192459 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 5/8/2008 5:47 AM |
|
2/10/2015 2:59 AM | |
Joined: 5/1/2013 Last visit: 8/29/2024 Posts: 428 Rating: (3) |
Could you tell me what is call distributors ?? Thank you. |