Hello Bilal; You could look at the following diagnostic FB126, both for Profibus-DP and Profinet. It reads the error messages in OB86 and provides information on rack and station failures; plus, it gives you pre-programmed HMI screens that you can use to inform the operator of the status of your network. http://support.automation.siemens.com/WW/view/en/26996747 Hope this helps, Daniel Chartier |
This contribution was helpful to3 thankful Users |
3/16/2009 12:05 PM | |
Joined: 9/27/2006 Last visit: 9/22/2024 Posts: 12282 Rating: (2685)
|
Hello Bilal; Here is the information you requested: -No of the DP station: the Profibus address of the node -Logical base address: the Diagnostic address of the node, attributed by the Profibus configurator (in HWConfig editor) NOTE: this logical base address is often refered to a LADDR when used as a parameter in a library function (FC, FB, SFC, SFB). Your idea of using OB86 will work, with a little dediaction. You couls also look at this sample program for reading a DP slave's diagnostics from OB82 (Diagnostic OB): masybe you can study it for use in your program. http://support.automation.siemens.com/WW/view/en/2190197 Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
3/16/2009 12:54 PM | |
Posts: 557 Rating: (64) |
HI find the attachment, having aready madeplc program. any doubt revert back. regards AttachmentOB86.zip (3640 Downloads) |
This contribution was helpful to3 thankful Users |
3/17/2009 1:35 PM | |
Posts: 22 Rating: (2) |
Hi you cantry this one. Only it is posible that the station no, has to be corrected to Hex notation AttachmentOB86.ZIP (2263 Downloads) |
This contribution was helpful to1 thankful Users |
3/18/2009 9:49 AM | |
Posts: 157 Rating: (10) |
Dear NSLaur, Thak you for your reply, but how i can open this file "OB86.AWL"?? Regards, BilalD |