5/18/2009 11:38 AM | |
Joined: 3/18/2009 Last visit: 5/6/2024 Posts: 306 Rating: (94) |
It should be possible. It will depend on what you want to actually achieve.
Look at WinCC Options in theST80 catalog(Page 4/71 and 4/73)
More documents on the above can be downloaded fromhere.
"MS SQL2005 Service Pack 2 for WinCC V7.0" |
5/18/2009 12:49 PM | |
Posts: 178 Rating: (5) |
Have you looked at using OPC or Simatic NET Station Manager ? |
5/18/2009 2:01 PM | |
Joined: 3/18/2009 Last visit: 5/6/2024 Posts: 306 Rating: (94) |
Yes, any other direct access, if possible, will be unsupported.
What do you mean when you say "database"? If you are only interested in current process values then as gbs suggests, OPC DA will be a free option (OPC DA server is free with WinCC). But if you want access to historical data (tag logging, alarm logging...) you need connectivity pack. Now, I do not know your application, but if you want something on mobile device through internet connection, you may also want to have a look atAdvanced IT - CPs (CP343 or CP443). With them you have many possibilities, includinnghttp access with java.(moreexamples in application and tools section) You will then not require WinCC. |
Last edited by: daga at: 5/18/2009 2:06 PM |
|
5/18/2009 3:54 PM | |
Joined: 5/18/2009 Last visit: 9/21/2023 Posts: 70 Rating: (2) |
OPC DA sounds interesting. Can you direct me to something i can look at(manual/example)? Thanks |
5/18/2009 4:52 PM | |
Posts: 178 Rating: (5) |
WinCC V7 includes OPC and OPCChannel pdf located in the installed WinCC documents folder. Happy reading... |