Joined: 11/17/2010 Last visit: 9/12/2024 Posts: 216 Rating: (40) |
Hi, Take a look to the link here part Digital outputs. Apparently maximum is 0.5A. 1.5A is consumption of the CPU (On internet consumption of the CPU is 1.5A and into manual consumption is 2A) Where is the truth ? Regards. |
Last edited by: Panov69 at: 6/23/2015 3:31:58 PM |
|
6/23/2015 4:07 PM | ||||||||||
Posts: 5225 Rating: (1192) |
Please have a look at: [LINK]
To look out for is that the specification is for resistive load. If you however are switching a inductive or capacitive load.. w |
|||||||||
This contribution was helpful to1 thankful Users |
6/23/2015 5:07 PM | |
Joined: 11/17/2010 Last visit: 9/12/2024 Posts: 216 Rating: (40) |
Sorry, I checked the wrong reference. Thanks to William_B to have corrected my post. |
This contribution was helpful to1 thankful Users |
10/8/2016 4:13 PM | |
Posts: 14 Rating: (1) |
Hi I think you can use following table for out put relay (AC/DC) for ohmic and inductive load.I think you can use 2 A for 24 vdc but number of operating cycle change. best regard AttachmentEXTRACT_S71200 FW4 System Manual (201403).pdf (342 Downloads) |