6/16/2011 9:08 AM | |
Posts: 487 Rating: (36) |
Basicaly there are two red LED on ( both sides) and two red LED flashing and yes should reset automatically when fault goes away. |
6/22/2011 2:47 PM | |
Posts: 1547 Rating: (129)
|
Hello, if the problem appears on the DP/DP Coupler, do you have also problems on other DP-Sales on the net? If the DP/DP Coupler is at the end of the Network check the termination and grounding of DP/DP Coupler and PROFIBUS cable. More information about grounding you will find here: SIMATIC NET PROFIBUS Network Manual System Manual Refer for that part Appendix C.6 regards Rated X |
6/27/2011 2:20 PM | |
Posts: 487 Rating: (36) |
If , one side of the pribus , you poweroff the last slave you get a bus fault but when this slaveis restarted then the fault on the bus coupler does not reset automatically , you have to pull the cables out and put them back and this is not a good solution |
6/28/2011 12:18 PM | |
Posts: 1064 Rating: (72) |
Have you tried to replace the dp-dp coupler? as it has been said before it should reset itself |