11/29/2018 4:12 PM | |
Joined: 10/1/2013 Last visit: 4/25/2024 Posts: 605 Rating: (71)
|
Ok, so for a S7-1500 and a RF380R I'd suggest to use the PROFINET communication module RF180C (see attached screenshot) since you just can't connect the reader directly to the PLC. You will only have to configure the PLC and communication module in TIA Portal. Just plug reader into the module. To control the reader I suggest to use the "Ident blocks". Here's an example on how to use the blocks: |
11/29/2018 4:47 PM | |
Posts: 23 Rating: (0) |
I've check with the colleagues the plc model and is a 1215C DC/DC/DC (6ES7 215-1AG40-0XB0) And with the plc i have a RF380R (6GT2801-3AB10) and (but im not sure at this point) a RF340T. |
11/29/2018 5:04 PM | |
Joined: 10/1/2013 Last visit: 4/25/2024 Posts: 605 Rating: (71)
|
Ok, with S7-12xx you'll need the RF120C communication module. And here is the how-to example: The transponder doesn't matter. Which ever RF3xxT it is, it'll work. |
Last edited by: Owei at: 11/29/2018 5:05:24 PM |
|
11/29/2018 5:25 PM | |
Posts: 23 Rating: (0) |
And where i can find the RF120C gsd ? Or I don't need it ? |
11/30/2018 4:00 PM | |
Posts: 23 Rating: (0) |
I can told you this only when all is plugged and ready ! I have the Reader in a box near me now eheh. |
12/5/2018 3:04 PM | |
Posts: 23 Rating: (0) |
No doesn't work. The green led on the 380R continue to blink. Can't understand why. |
12/6/2018 11:37 AM | |
Joined: 10/1/2013 Last visit: 4/25/2024 Posts: 605 Rating: (71)
|
Did you call Reset_Reader? What are the outputs of the reset block? |
Last edited by: Owei at: 12/6/2018 11:37:52 AM |
|
12/6/2018 11:57 AM | |
Posts: 23 Rating: (0) |
Here's a screen. And when i execute the reset the RF120 give me an error. |
12/10/2018 9:07 AM | |
Posts: 23 Rating: (0) |
Yes, sure. Sorry for the late answer. Attachment18.056 Carico e Scarico Manuale OP45_1.zip (275 Downloads) |
12/10/2018 4:20 PM | |
Posts: 23 Rating: (0) |
My code is fine then. So the problem is the cable ? How to test it ? Unfortunately I don't have a spare cable here. |
12/10/2018 4:37 PM | |
Joined: 10/1/2013 Last visit: 4/25/2024 Posts: 605 Rating: (71)
|
Might be the cable or the reader. Do you have a spare reader to cross check that? |
12/10/2018 4:43 PM | |
Posts: 23 Rating: (0) |
No, no spare reader avaiable. |
12/10/2018 5:40 PM | |
Joined: 10/1/2013 Last visit: 4/25/2024 Posts: 605 Rating: (71)
|
Attached you'll find the project I used. I basically just swapped the PLC. Even though I had a RF310R it also worked with RF380R in the TO configuration. So your problem must be caused by the cable or the reader. Edit: Is your RF180C shining green or blinking green? Attachment18.056 Carico e Scarico Manuale OP45 siemens.zip (233 Downloads) |
Last edited by: Owei at: 12/10/2018 5:41:51 PMLast edited by: Owei at: 12/10/2018 5:42:43 PM |
|
12/10/2018 5:47 PM | |
Posts: 23 Rating: (0) |
Before the reset comand on the 120c both the 24V and DIAG led are green, no blinking. |
12/10/2018 5:50 PM | |
Joined: 10/1/2013 Last visit: 4/25/2024 Posts: 605 Rating: (71)
|
Ok. In this case it must be reader/cable. |
12/10/2018 7:04 PM | |
Joined: 10/1/2013 Last visit: 4/25/2024 Posts: 605 Rating: (71)
|
Would be nice if you share the outcome of this support request. |
12/11/2018 1:06 PM | |
Joined: 10/1/2013 Last visit: 4/25/2024 Posts: 605 Rating: (71)
|
It's always just array of byte. |
12/11/2018 3:13 PM | |
Posts: 23 Rating: (0) |
Cable checked today, seems ok. but error still remain. |
12/12/2018 2:56 PM | |
Joined: 10/1/2013 Last visit: 4/25/2024 Posts: 605 Rating: (71)
|
In this case it should be the reader |
Last edited by: Owei at: 12/12/2018 2:56:21 PM |
|
12/13/2018 11:23 AM | |
Posts: 23 Rating: (0) |
We proceeding now with the modules and cable replacement. |
12/15/2018 1:54 PM | |
Posts: 23 Rating: (0) |
Reader changed. All is working fine now. |
This contribution was helpful to2 thankful Users |