Hello, from the manual: F30045 Power unit: Supply undervoltage Message value:%1 Message class:Supply voltage fault (undervoltage) (3) Drive object:SERVO, SERVO_AC, SERVO_I_AC Reaction:OFF2 Acknowledge:IMMEDIATELY (POWER ON) Cause:Power supply fault in the power unit. - The voltage monitor signals an undervoltage fault on the module. The following applies for CU31x: - the voltage monitoring on the DAC board signals an undervoltage fault on the module. For S120M, the following applies: - This message is displayed for undervoltage or overvoltage. Remedy:- Check the power supply of the power unit. - carry out a POWER ON (power off/on) for the component. - replace the module if necessary. List Manual S120/S150 - Siemens AG Chapter 4.2 |