Joined: 12/18/2014 Last visit: 9/22/2024 Posts: 33817 Rating: (4201) |
Maybe indirect addressing? Can you upload the S5 Project as a zip file? |
4/9/2020 4:53 AM | |
Joined: 10/7/2005 Last visit: 9/22/2024 Posts: 3021 Rating: (1054)
|
Hi Peejay having COM 95F would help, but in the end you can also work out the settings it creates by manually evaluating DB1, see chapter 9.3 of the S5-95F manual for details. In your case I suspect the non-failsafe Q33.0 to Q33.3 outputs are used for short circuit tests and thus not addressed directly in the S5 program (your are looking for a "KT:" parameter block in DB1 to verify this, see also page 345 of above manual). Usage of FB252 in the S5 program would be another hint that these outputs are indeed used for short circuit tests and chapter 9.2.9 of the manual has all the gory details on FB252. |
Cheers |
|
This contribution was helpful to1 thankful Users |
6/21/2020 4:27 AM | |
Joined: 10/7/2005 Last visit: 9/22/2024 Posts: 3021 Rating: (1054)
|
Hi Peejay as per COM 95F manual: "The COM 95F parameterization software has been created to save you the trouble of editing DB 1. You simply fill in some user-friendly screen forms in interactive dialog with COM 95F and the software then generates DB1 with the required parameters" While COM 95F also helps with the the system documentation and error diagnostics, there is no "hidden" safety program that is only visible with COM 95F (DB1 creation is really all there is to it) |
Cheers |
|