2/24/2016 8:15 AM | |
Posts: 10 Rating: (0) |
Please Help anyone |
2/24/2016 8:45 AM | |
Posts: 5225 Rating: (1192) |
My friend Duris told me the other day (smile) |
2/24/2016 9:24 AM | |
Joined: 4/28/2015 Last visit: 2/7/2024 Posts: 10533 Rating: (820) |
Hello, hope this will be helpfull to you Ygor simply set correct HW module ID. You can also put correct HW address to Port via click on that Port, then you can have prepared that PORT as parameter, but you must correctly set value. Update: but better help will be William's pictures with arrows (red/blue) showing exactly needed steps AttachmentMB_cfg.zip (573 Downloads) |
Last edited by: Duris_I at: 2/24/2016 9:33:19 AMWith best regards... |
|
2/24/2016 8:48 PM | |
Posts: 10 Rating: (0) |
Hi Here are some screenshots of the code. As i said before I want to read three current measurement from the Relay. According to SEL 751A Relay manual appendix E Table E.34 the User Map Register Values are in registers 126 to 250. Also according to S7-1200 manual Table 12- 69 Modbus functions, if I use MODE zero I should be able to read the Read Holding registers 40001 to 49999. That is why in my code i made it so it reads the first 3 values on the Relay. For The Master REQ I used a switch, to enable any time I want to read. But I keep getting a 8180 Invalid port ID value ERROR on the Master. Not sure if my Code is totally wrong or the Relay itself is not communicating. Thanks
Today I used ModScan64 to see in the Relay could communicate with My PC and it did. At first I was worry that my logic on the Relay was wrong. But given that it work with ModScan64 (I was able to Read and write to it). I am almost certain that something is wrong with my code. I am very new to PLC coding and please forgive me for my simple questions. Thank you again Duris_I and William_B for the support. I am not getting a 8180 Invalid port ID on the MB_COMMNDLOAD anymore. But my MASTER block is still given the 8180 error. Do I need to add more to my code? |
Last edited by: Ygor0191 at: 2/25/2016 3:36:49 AM |
|
This contribution was helpful to1 thankful Users |
2/29/2016 4:03 AM | |
Posts: 10 Rating: (0) |
Hi William_B What do you mean by "Do consider putting an auxilary flag in to trigger the load function (in parallel) with the first scan bit." Thank you |
3/7/2016 4:03 AM | |
Posts: 10 Rating: (0) |
Hi William_B Attached is the last version of my code. I followed your advice, but it did not work :( I am a little frustrated, I know that the SEL 751A relay works via modbus because I tested it with modScan64 software on my computer. The comm load block runs with no error, but the Master block is still given me that 8081 invalid port id error. I made sure I inputted the correct slave ID, check the Rs232 cable, and to me my code made sense, I should be able to read. One interesting finding is that the CM1241 rs2323 communication module on the PLC, Tx and Rx LED do not blink at all when I run the program. I have consulted with a professor at my university and he did not know how to help me. thank you again for your support Hope to hear from you soon. Regards Ygor AttachmentModbus code.zip (346 Downloads) |
3/7/2016 7:55 AM | |
Posts: 10 Rating: (0) |
Hi william_B What do you mean by "review x3 pins hidden from view on the MASTER instruction" I have look over the master block and Cant seem to find the hidden pins? Could you clarify this for me? On another note: I was looking into the S7-1200 manual the section 12.3.5.1 Configuring the communication module. In this example, an S7-1200 CPU communicates to a PC with a terminal emulator through a CM 1241 RS232 module. I have come to realize that I never did any configuration of the CM1241. All I did was detect the modules attached to the PLC, then look up the hardware ID for the module and make the COMM and MASTER blocks respectively. My question know is do I need to Program the PtP communications before using Modbus rtu communication? configure the PORT_CFG. SEND_CFG AND RCV_CFG blocks? because if so, that might be my issue. I have attached the section of the manual so you can refer to what I have said. A thousand thanks for following up to my questions. Attachmentmanuel-plc-siemens-s7-en.pdf (405 Downloads) |
3/12/2016 12:45 AM | |
Posts: 10 Rating: (0) |
Hello Duris_I and William_B I have attached some pictures of the program running . As you may see, the COMM_Load runs with no error. The Master is still giving me the 8180 (invalid port ID or error with Comm_load instruction). I also included a picture of the CM1241 rs232 comm module, as you can see the LED lights for Tx and Rx dont blink at all while the program is running. Regarding the hardware as William_B suggest, I made the Null modem connections shown in picture. But I am still getting the error. I am not sure whether is my code that is poorly written or maybe the CM1241 it self. Are there programs written to test the CM1241? I want to make sure is functioning properly. Note: I am running the code I poster previously Thanks again for the support Gentlemen Attachmentmodbus_Error.pdf (482 Downloads) |
3/12/2016 7:01 AM | |
Posts: 5225 Rating: (1192) |
Hi. Sad.. it is sad to hear that the users' forum is not of help for your case. I am sorry about that. I suggest you take the next step. Come in contact with the official Siemens Support: https://support.industry.siemens.com/my/ww/en/requests#requests You will fill out some information and have the opportunity to state your problem. Make sure you include the hardware part numbers and the software versions and licensing you use. The first response from Siemens Support will quote pieces from the manual. The first response is rarely helpful to those of us who has done their homework. There is no way to bypass this first response. Be respectful and reply.. you can add your program for them with this reply. On average Siemens Support is better than what I have seen from others. If all goes well, you should have an answer in a few days. I ask you to return to the users' forum and inform us what the findings were. Good luck. w |
Last edited by: William_B at: 3/12/2016 8:49:27 AMAdded the contact address for Siemens Support |
|
3/12/2016 8:43 AM | |
Joined: 4/28/2015 Last visit: 2/7/2024 Posts: 10533 Rating: (820) |
Agree with William, but let me say 'sad' also, because still don't know answer about COM settings on PC side application from you Ygor, also if you really had .DONE status ON checked, not depended that Status 16#0000. If you really didn't execute that MB_LOAD instruction, you still probably have 16#0000. Sry, but this is simply waste of time, we simply can't again and again ask and answers aren't here. Also if we take your TIA version, you didn't specify what kind of SP or updates you have, or not? Good luck. Last addition: look at that pdf, maybe this can be also helpful to you. modbusRTU with Delta Temp controller |
Last edited by: Duris_I at: 3/12/2016 8:54:37 AMLast edited by: Duris_I at: 3/12/2016 8:58:12 AMWith best regards... |
|